I'm running power for my Syncrowave 200.

 

I'm going with a 60 amp breaker, and 6awg 2 wire/w ground wire. I'm running the outlet max of 10 feet from the service panel.

 

Miller says it will draw 54 amps, but says to run an 80 amp normal operating breaker.

 

From what I've found other places, a 60 amp breaker will be fine, with 6-2 wire.

 

My only concern is that the only plugs there seem to be are 50AMP.

 

Now, wouldn't I want the plug to be at least rated for 60 amp? Or because the machine will not draw more than 50 amps, because of the duty cycle that it will be okay?

Link to comment
Share on other sites

I BOUGHT AN OLDER MILLER 330 AMP TIG WELDER AT A DECENT PRICE, BUT IT WEIGHTS 900 LBS AND REQUIRES A 100 AMP FEED

 

I saw the price of 100 amp disconnect plugs at the local electrical supply and said thats nuts! a plug and socket costs $500???

 

I ran into the same problem with my 100 amp feed on my 330 amp tig, the correct plug/socket listed at almost $500 at the local electrical supply

(THATS TOTALLY NUTS)

so I thought about it a bit and bought three of these TWIST CONNECTORS FOR WELDING CABLES

 

http://www.fastenal.com/web/products/detail.ex?sku=0812198

 

theres a MALE and FEMALE END to each TWIST CONNECTOR

 

BTW they cost me about $20 each at the local welding supply

 

painted two red and one green

 

ran three feed wires in conduit to a large plastic storage box with a cam loc front pannel

 

ran a 50 foot long tripple feed cable attached to the welder inside 2" flex tube

 

the green is ground the two reds are power, think about it a bit, it works great, I simply leave the 100 amp electrical braker off , unless they are connected to the welder and you can,t screw it up because its both color coded and the ends won,t connect wrong physically

 

hooked up the green one from the wall connection with the extended male side of the connector extended, ran the two red feed with the enclosed female side from the power

http://www.fastenal.com/web/products/detail.ex?sku=0812198

 

walls got two red female and one green male connector, welders got a 50 ft extension cable with two red male and one green female connector

 

the 100 amp breaker keeps power from the connectors unless they are connected and the connections are made in a 18" plastic water resistant electrical box with a lockable lid mounted 4 ft above the floor

 

just use the correct ga. I used 00 GA

 

 

http://www.powerstream.com/Wire_Size.htm

 

THE 50 FT TAIL ON THE WELDER ALOWS ME TO MOVE THE TIG ANYPLACE IN THE SHOP AS THE CONNECTORS ON A WALL MOUNT NEAR DEAD CENTER BETWEEN THE GARAGE DOORS

 

NEAR THE TRACTOR IN THIS PICTURE

 

garage8.jpg

 

 

IVE got a MANUAL DISCONNECT,in the line between the breaker and the connection box, with a big sign, (emergency disconnect) I just didn,t get into that as it seemed to complicate things in the description of the circuit

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...